- What is the preferred systems modelling software for CSC/VSC power electronics, and how is validation of these models typically carried out?
Angela P P, Lead Asset Lifecycle Engineer – HVDC, National Grid, UK: Most TSOs use a mix of simulation environments that support both RMS level and electromagnetic transient modelling, because different studies require different levels of detail. Suppliers typically provide models that include the full converter control structure so that steady state and dynamic behaviour can be assessed consistently.
Validation is usually done in stages: first by checking the control block behaviour against the design intent, then ensuring consistency across the different modelling environments, and finally comparing the model response with factory or commissioning data.
Claus Leth Bak, Professor, Head of Section of Power Systems and Microgrids, Aalborg University (AAU), Denmark: EMT tools like PSCAD or similar. Validation with measurements from real life.
- VSC vs CSC for HVDC: Which system has higher losses, and which is more economically viable for future power networks?
Angela P P: When it comes to economic viability, it’s very case dependent. CSC can be more cost efficient for long distance bulk transfer on strong grids, while VSC often becomes more viable where controllability, weak-grid operation, renewables integration, or multi terminal capability are required. So the ‘better’ option really depends on the specific network needs and project context.
Alexander Tsylin, Senior Lead Specialist for Plant Control and Protection Systems, Ørsted, Denmark: For today’s HVDC technology, VSC-based HVDC has higher losses, while economic viability depends on the application: classic CSC/LCC is still cheaper for a few very large point‑to‑point links, but VSC is generally more attractive for future, flexible grids as it can connect weak grids and enable multi-terminal and meshed HVDC systems.
- With Denmark being the leader on integrating electricity from the wind to their local grid...are there any good practices from Denmark that the UK can learn from?
John Wright, Europe and Africa Technical Application Engineering Leader & Product Growth Leader, GE Grid Solutions, UK: As we transition to digitisation all information is good - the key is that we share it. From a protection point of view, the teams in Denmark have valuable experience and are already sharing.
Alexander Tsylin: Denmark’s success in integrating high shares of wind power is driven by strong transmission planning, close TSO–DSO coordination, effective use of interconnectors, and advanced system operation supported by accurate forecasting and flexible markets. A key lesson for the UK is that high wind penetration can be achieved reliably through early grid reinforcement, operational flexibility, and system-wide coordination, not just by adding more renewable generation.
- When we can add many SMRs and/or fusion plants to the grid, do you think that we would/should see a return to a simpler, top-down grid?
Alexander Tsylin: From my perspective, adding many SMRs and/or fusion plants would not justify returning to a “simpler, top-down grid”, but rather rebalance the system. The future grid will likely be more hybrid and distributed, even with significant SMR/fusion capacity as such plants are designed for localized deployment at the transmission level, not fully centralized mega-plants.
- How much longer can 70/80-year-old assets last? How widespread are such old assets?
Alexander Tsylin:70/80-year-old substations and power plants remain widespread, with high proportion of primary assets (transformers, breakers, turbines) still operational after 40-80 years, capable of 10–20 more years through condition-based maintenance and refurbishment.
Secondary systems (protection, SCADA) are the limiting factor, typically lasting only 15–30 years before obsolescence forces replacement due to technological change, cybersecurity requirements, and support limitations, making them the main drivers for refurbishment even when primary assets remain mechanically sound.
As a result, modern asset management increasingly focuses on selective life extension of primary plant combined with periodic renewal and digitalisation of secondary systems to maintain reliability, compliance, and operability.
Angela P P: When the assets are in good condition, lightly stressed, operated within design limits and regularly maintained, they perform reliably for several decades. However, lifespan is highly case specific and longevity depends on several varying factors such as mechanical wear (in electromechanical devices), component ageing (capacitors, coils, contacts), environmental exposure (humidity, temperature), maintenance history etc. So while many P&C relays can physically last far beyond their nominal design life, their true remaining life varies by asset and condition and not by age alone.
- How do you think that in the future, the type of job of a PAC engineer will be changed, since more involvement of automation will definitely effect the current job description of PAC engineers?
John Wright: For many years a mixed skill set will be required as we have a mixed generation of PAC. However, as we move towards digitisation knowledge of communications and standards will be critical in addition to basic power system and protection knowledge. You will also see a change in the way we test systems - the tools are more computer based and require a different skill set.
We will start to see more specialists, such as network engineers with deep knowledge of the communications network. Critical for designing, testing and debugging systems. These Engineers may not have the detailed protection knowledge. Also, we are all moving towards a common goal if interoperability to IEC61850 - this standard describes the Engineering process, so skills will develop in line to meet the standard.
Alexander Tsylin: Please take a look at CIGRE TB "977 - Education, qualification and continuing professional development of engineers in protection, automation and control" for more insights.
- Are there any near future plans to implement complete digital substations in UK?
John Wright: Many in the UK are already on this journey - it is the scale that is varying - Station Bus is common practice - Process Bus is somewhere between pilot sites and bays integrated into a conventional substation. For others Process Bus will be the standard going forward. It’s important to understand that we have the capability to deliver DSS - its sometimes a matter of economics and capabilities of Engineers.
- Traditionally, electrical design engineers focused on calculations, equipment selection, and hardwired protection and control schemes. With the shift toward digital substations, IEC 61850, and virtualised PAC systems, how do you see the role and responsibilities of design engineers evolving? What new skills, design steps, and interfaces should engineers prioritise to successfully adapt to this digital transformation?
we will start to see more specialists, such as network engineers with deep knowledge of the communications network. Critical for designing, testing and debugging systems. These Engineers may not have the detailed protection knowledge. Also, we are all moving towards a common goal if interoperability to IEC61850 - this standard describes the Engineering process, so skills will develop in line to meet the standard.
- Considering 61850 holistically, are their any development towards:1. interchangeability of relays from different vendors,2. New substation are adopting PTP for time synchronization to achieve T5 accuracy as recommended by IEC 61850, What are the challenges in integrating the legacy systems to achieve the same instead of say IRIG-B or SNTP and how is the industry working towards achieving this with the legacy IEDs?
Alexander Tsylin: Yes, there are certain developments in both areas:
1. Progress exists through UCA IUG interoperability tests and Edition 2 conformance certification, but full "plug-and-play" interchangeability remains limited. GOOSE/SV exchange works reliably between certified IEDs from different vendors, though manual SCD file edits are often needed for complex schemes. CIGRE B5.69 TB 949 documents multi-vendor process bus pilots with 80-90% success rates.
2. Legacy IEDs typically support IRIG-B and SNTP, have hardware limitations and often lack PTP support. Integrating the legacy systems requires use of protocol converters/gateways.
- What is the importance of studying the fault signatures and waveform records on systems with high penetration of IBRs? How do we assess the reliability of Protection Functions such as Distance and Directional Protection on systems with high penetration of IBRs?
John Wright: The art of protection is distinguishing between a healthy and fault condition. Many relays look at the fault signature during a certain operating window - often determined by the filtering techniques used i.e. fourier etc. If the signature is dynamic during the operating window then an in correct decision can be made or if the wrong filtering techniques are used then the decision comes too late and the plant is already damaged.
In addition to this as discussed in the webinar certain types of protection use techniques to ensure that they operate correctly in certain conditions - i.e. polarising techniques. One example is the use of negative phase sequence - depending on the type of REN or the country the control system that provides negative phase sequence support may vary - this can result in an unpredictable result. Therefore we study the signatures to make sure the algorithms work correctly. They can be tested in many ways - off line modelling to hardware in the loop.
- I'm new to electrical protection, coming from the world of electronic design engineering (circuit design). It strikes me that it would be fairly trivial and relatively low cost to integrate injection sets into switchgear such that protection maintenance could become a semi-automated task, removing the human from the loop somewhat . Are we starting to see this trend in the protection industry please (possibly more in distribution, due to closely 'clustered' groups of relays at feeders)?
Alexander Tsylin: While fully integrated secondary-injection hardware inside switchgear is not widespread, the industry is moving toward semi-automated and remote protection testing. Modern IEDs already include extensive self-diagnostics and built-in test functions, and digital substations using IEC 61850 (process bus, test modes) make automated functional testing increasingly practical.
The main barriers to full adoption are safety assurance, legacy equipment, and utility confidence that automated tests are equivalent to traditional secondary injection. As a result, the near-term trend is toward IED-driven, software-based and remotely controlled testing.
- How soon do you see Virtual RTUs coming in play in majority of utilities, in order to scale data acquisition/aggregation?
John Wright: Virtualisation is gaining traction as it can save Engineering time, reduce time on site and reduce down time during any reconfiguration. It gives a level of comfort that the system is working correctly without having large amounts of equipment. So in theory the more of the system that is virtualised the more efficient this process is.
Alexander Tsylin: Virtual RTUs might come into play close to 2030s.
- With the advancement of IEC61850 communications-based systems for Prot, Ctrl and SAS and now the extension to the Process Bus with the use of Merging Units, at what stage is the adoption of Power Utilities for the Virtualised environment for the traditional Protection, Control and Substation Automation?
- What are the new research areas that will eventually emerge from this new technology/systems for the academic communities?
Alexander Tsylin: New PAC technologies driven by high IBR penetration, WAMPAC, and centralized or virtualized architectures are opening major research areas for academia, including protection and control co-design for low-inertia systems, model- and data-driven protection methods, wide-area and system-level protection concepts, AI-assisted and explainable PAC functions, cyber-physical security of protection systems, and PAC-enabled asset management and digital twins.
Overall, the field is shifting toward system-aware, software-defined, and data-informed PAC, requiring closer integration of power systems, control, communications, and software engineering research.
- What new technologies are planned for implementation over the next 5-10 years by National Grid? Is it possible to provide a bit more detail?
Angela P P: Over the next decade we expect to focus on building confidence in the next generation of PAC architectures, particularly around process bus and virtualised or centralised PAC systems. The industry has already laid the digital foundations with numerical IEDs, and the next step is progressing through process bus pilots and open loop virtualised substation trials to understand performance, operational impacts, and long term benefits. These technologies support greater standardisation across architectures, interfaces, and data models, making future upgrades and lifecycle management more manageable.
At the same time, a heavier reliance on digital systems increases the importance of cybersecurity, so secure architectures, segregation, access controls, and continuous monitoring will be central considerations.
Overall, adoption will remain incremental and risk based, reflecting the long lifecycles, interoperability requirements, and operational practicality that shape decision making.
- In Denmark, what is the % of non-sync generations normally and max? How do you make sure the system's operational stability when we have high penetration of non-sync gens?
Alexander Tsylin: Denmark operates with annual average % of non-sync. generation of 55-65%; quite frequently (during some hours) it can reach 80-100%; observed maximum is >100%.
Success in integrating high shares of non-sync. generation and system's operational stability are driven by strong transmission planning, close TSO–DSO coordination, effective use of interconnectors, and advanced system operation supported by accurate forecasting and flexible markets.